The current output of the charge controller will depend on the input power. Just because it is a 40A controller does not mean it will always output 40A.
I would recommend consulting the battery manufacturer or spec sheet to see the individual battery's charging parameters.
The amount of current each battery will see will also depend on the wiring configuration. Just because two batteries are wired in parallel does not mean that the current gets split evenly.
This link has some good information regarding battery wiring.
www.smartgauge.co.uk/batt_con.htmlAfter you find your battery's specs and the input power you plan to use, please come back so we can get this figured out.
Renogy Tech Support
SR
SR,
That link to Smart Guage is great..... I love when folks use pictures and speak plainly. In the beginning you don't need a lot of scientific notation but a couple of drawings and 30 words can speak volumes.
Right now I simply have 2 small banks both built like this.
2 150Ah in parallel
Interconnects are 13" 4/0 +/+, -/-
CC is wired to + of 1 battery and - of the second.
A very basic setup.
The link you provided gives me several options IF and when I need to add/reconfigure to suit my needs.
HERE"S A QUESTION:
My batteries have short terminals so adding a third lug is not an option. I imagine I could fashion a small copper bus in order to add another set of lugs. Again, only as the situation demands.
That link to Samrt Guage is a keeper.