Post by Jayc on Apr 9, 2015 10:28:25 GMT -8
I have a PWM30CC controller and I want to have the load manually switched. My question is if I set the mode to manual and the battery gets low and the controller shuts off the load, will it turn the load back on when the battery is topped off, or would I manually have to turn it back on?
|
|
|
Post by Jayc on Apr 16, 2015 14:28:41 GMT -8
Anyone have a solution for this scenario? Basically unattended load with low voltage disconnect and reconnect in a solar charger...
|
|
|
Post by Admin on May 8, 2015 8:30:15 GMT -8
Hello Jayc,
I apologize for the delay. The controller will reconnect the load when the battery voltage returns to 12.6V.
Renogy Tech Support SR
|
|