Post by sozo13 on Jun 2, 2015 10:38:57 GMT -8
I have a 40 amp tracer running 2x250w panels into a new 440 ah 12v bank I also have a 20 amp tracer mppt on 2x 120w panels on a single soon to be dead 12v battery
can I hook both of these up to the single 12v battery bank?
so far ive heard yes they will work great together
no they will conflict thinking ones charging state is a full bank
and omg no you moron you could die ...or something along those lines
so I came to the source will this work well or not at all
|
|
|
Post by Admin on Jun 15, 2015 15:16:59 GMT -8
Hello Sozo13,
Yes you can hook both these charge controller to a single battery bank.
O.C
|
|
|
Post by abooza69 on Aug 11, 2015 11:45:20 GMT -8
Ok, so do you have a schematic on how to do this?
|
|
|
Post by Admin on Aug 11, 2015 13:26:44 GMT -8
Hello Sir, Unfortunately I do not have a schematic but all you will need to do is connect the output of each controller to the positive of the first battery and the negative of the last battery in the string. O.C
|
|
|
Post by abooza69 on Aug 14, 2015 9:24:03 GMT -8
Thank you.
|
|
|
Post by abooza69 on Aug 15, 2015 14:10:45 GMT -8
One more qiestion: if I have two controllers installed, do I need two meters as well or is one enough?
|
|