Post by ds on Feb 16, 2018 12:03:29 GMT -8
I have five (5) RNG-110D panels that I want to connect to a Commander 40 amp charge controller (12VDC). Am I missing something or do I need seven (7) MC4 branch connectors to parallel the panels ? Is there another way ?
Thanks, DS
|
|
|
Post by tattoo on Feb 16, 2018 12:46:51 GMT -8
You will need 8 connectors I'm fairly sure... Any reason why your going parallel? With series you won't need any connectors...
|
|
ds
New Member
Posts: 3
|
Post by ds on Feb 16, 2018 18:32:01 GMT -8
Series is fine with me, I was worried about the voltage being too high. If the controller can take it, series sounds good. Thank you
|
|
|
Post by tattoo on Feb 17, 2018 7:01:58 GMT -8
I had the same set up a while back.... It worked just fine...
|
|