Post by timsim00 on Dec 21, 2016 13:58:43 GMT -8
I currently have an issues where if I turn off my inverter for my 5 hours of peak sun, I can charge my batteries to 100% (14+ VDC). As soon as I turn on my Renogy 2KW inverter, the batteries drop to close to 60% and holds steady, this is without any load on the inverter at all.
Any thoughts?
Panels:
4 100W 12V Renogy Mono panels
Charge Controller:
40A MPPT Renogy CC
Inverter: Renogy 2K Watts PSW
Batteries:
4 6V 230AH batteries in series and parallel for a 12V system @ 460AH
PS. I am about to install (2) 150W 12V panels in parallel with my current four panels in a parallel series. So, my total Amps per hour now is about 20A, with the new panels will be closer to 36Amps per hour.
|
|
k0vwa
New Member
Posts: 5
|
Post by k0vwa on Jan 6, 2017 7:22:40 GMT -8
The manual says it only uses 1.7A on idle so that much battery capacity shouldn't drop to 60% when only providing 1.7A. Can you tell us more about what is indicating the batteries at 60%?
|
|
|
Post by rabird on Jan 6, 2017 13:05:36 GMT -8
No one knows how these folks determine % state of charge, certainly not while being discharged. The readings are bogus and should be ignored.
Best for me to use battery voltage as an 'indication' and experience how loads & time drop voltage
|
|