Post by muttmaster on Oct 7, 2017 16:37:49 GMT -8
I just got a 100 watts suitcase with 30 amp Adventurer controller. It came with what looks like 12 awg wire with inline fuse rated at 10 amps at the battery clip. I upgraded to 10 awg because I need longer extension. I want to use 30 amp fuse inline to battery. Just wondering why Renogy included only 10 amp fuse, which is rated for 16 gauge wire.
|
|
|
Post by rabird on Oct 7, 2017 17:59:33 GMT -8
cheap sobs. Whom ever they get them from know that 100 watts ain't gonna exceed 6-7 amps in extreme cold/bright light so there is no reason to use a bigger fuse.
while 30A and 10g go 'together' there is noting saying you need to max the fuse rating to the wire size, it is ok to use a less fuse.
|
|
|
Post by muttmaster on Oct 7, 2017 18:29:27 GMT -8
Thanks Rabird for the advise.
|
|