Can I run a 5000 btus ac window unit with solar?
Posts: 12
|
Post by inhabor on Nov 5, 2017 18:00:50 GMT -8
I installed a 300 watts system in my vw bus. It worked fine for a few days. Today the charge controller shut off suddenly. It was running five 3 watts led ligths. The controller is a 40amps Rover and a Renogy 100hrs lithium phosphate battery. Any ideas why?
|
|
|
Post by rabird on Nov 6, 2017 4:21:54 GMT -8
nhabor, there is low voltage cut off if you are using the load terminals, if so the bottom led should light up. Cycle through the display to see if there is an error code.
|
|
inhabor
New Member
Can I run a 5000 btus ac window unit with solar?
Posts: 12
|
Post by inhabor on Nov 6, 2017 18:06:06 GMT -8
nhabor, there is low voltage cut off if you are using the load terminals, if so the bottom led should light up. Cycle through the display to see if there is an error codeIt It was working fine today when I got home.
|
|
|
Post by rabird on Nov 6, 2017 18:38:43 GMT -8
sp you can not report what the batt voltage may have been when it failed? or if there was an error code?
|
|
inhabor
New Member
Can I run a 5000 btus ac window unit with solar?
Posts: 12
|
Post by inhabor on Nov 24, 2017 15:53:36 GMT -8
Now I can. I just installed a Bogart meter.
|
|